Using the kVA/HP Code, A Voltmeter and Ammeter to Commission an Electric Motor
This process can be used with either new or repaired electric motors. Using the nameplate information of a three phase induction motor, you can obtain the current, horsepower and kVA/HP Code. These values can be used to calculate the inrush, or locked rotor, current of the motor. The ammeter and voltmeter must each have the ability to capture min/max readings. Connect the ammeter to Phase A and the voltmeter leads between Phase A and B with the ammeter set to capture max current and the voltmeter set to capture minimum voltage. Start the motor and obtain the results from both instruments.
The results are applied to the following:
![LRA](https://assets.rbl.ms/27903602/origin.jpg)
Table: kVA/HP Code AC Induction Motors
Results falling outside the locked rotor current range indicates rotor bar or stator winding faults, including workmanship issues.