Calculating Motor Load With A Voltmeter and Ammeter
Accurately evaluating electric motor load can be useful when troubleshooting conditions. In machines over 50% loaded this can be performed with a relatively good degree of accuracy with a True RMS voltmeter and ammeter, if more advanced instruments are not available. If you are using an ammeter or voltmeter with min/max capabilities, you can obtain peak loading, in variable loads, by taking your max readings across a full cycle of operation. Otherwise, the results are a snapshot of the point in time and cycle of operation.
Take voltage and current for each phase of the motor (Va-b; Va-c; Vb-c; Aa; Ab; Ac). Calculate the average of each:
Using the nameplate voltage (Vn) and current (An), the true load can be estimated as:
Howard W Penrose, Ph.D.
Howard W Penrose, Ph.D., CMRP, is the President of MotorDoc LLC, the Executive Vice President of MotorSight Corp, Treasurer of SMRP and Web Editor-in-Chief of the IEEE Dielectrics and Electrical Insulation Society. Howard has over 30 years in the electric machinery repair, design, materials, energy and systems industry and is an award-winning author. www.motordoc.com